03-11-2023, 10:43 PM
new indirect Heat-Flo has been running fine since Dec install.
The boiler return is hot to the touch. The hot water out is warm at best.
The boiler is a Slant-Fin Bobcat installed in Nov. 2010. Is has been running fine, but I have heard some clicking from within on occasion.
No Error is indicated on boiler. But it seems to be cycling a lot. Every 3 to 5 minues. Outside temp is indicated on the panel as 55º but it is 43º.
dhw shows a temp of 180 to 210º.
return shows 139º.
no temp is shown on boiler for dhw. I'd have thought the Heat-Flo has a sensor in it, but perhaps just the aquastat to send to the boiler.
supply water temp is 194º
wp is around 15psi
House heat is fine.
temp out of faucets is 85º. Whats wrong with this picture?
I just toggled the power switch to see if the Slant Fin needed a reset. n/c
The boiler return is hot to the touch. The hot water out is warm at best.
The boiler is a Slant-Fin Bobcat installed in Nov. 2010. Is has been running fine, but I have heard some clicking from within on occasion.
No Error is indicated on boiler. But it seems to be cycling a lot. Every 3 to 5 minues. Outside temp is indicated on the panel as 55º but it is 43º.
dhw shows a temp of 180 to 210º.
return shows 139º.
no temp is shown on boiler for dhw. I'd have thought the Heat-Flo has a sensor in it, but perhaps just the aquastat to send to the boiler.
supply water temp is 194º
wp is around 15psi
House heat is fine.
temp out of faucets is 85º. Whats wrong with this picture?
I just toggled the power switch to see if the Slant Fin needed a reset. n/c