I'm overloading my office and I know it. I've got one 20A circuit feeding this room. I could probably tap into the circuit of the adjacent room by punching a hole in the wall and putting an outlet in on this side.
That said, I'm trying to see if there's some other, possibly easier way to deal with it. Right now I've got two UPS's and three plug strips connected. They're not all full, some of the power bricks take up some space (eg, one plug strip has only two devices plugged into it.)
Overall I've got about 24 devices plugged in. Any idea how to best handle this?
TIA
Posts: 42,600
Threads: 545
Joined: Nov 2023
Reputation:
0
are the overhead lights on the same circuit? If so, switch to daylight CF bulbs, and maybe gain back 150 watts of available power. Or punch through the wall.
Posts: 21,860
Threads: 1,734
Joined: May 2025
Reputation:
0
I forget if they are or not... either way the entire house is pretty much CF now.
Posts: 21,860
Threads: 1,734
Joined: May 2025
Reputation:
0
I can't even tell what that is.
Posts: 42,600
Threads: 545
Joined: Nov 2023
Reputation:
0
suitcase generator. I keep forgetting that we never lose power here. But with you being from "up north" I figured you would know what it was.
Posts: 21,885
Threads: 1,109
Joined: Mar 2024
Reputation:
0
Well it's really not just the number of devices, but the total amps that they are drawing at any given time. If you are exceeding the limit for the circuit it would trip the breaker.
How many outlets are you using? Most regular outlets are rated for 15A. Divide your higher load devices between separate outlets if possible.
Make sure your extension cords are good thick gauge ones capable of supporting 15A loads. Same goes for the power strips. Thinner extensions and power strips will actually increase the load on the outlet because they will heat up under high loads, increasing resistance in the wire. UPS's draw power too. If you don't need them don't use them.
If you've got an outlet on the other side of the wall (from a different circuit) then you've pretty much got an outlet in your current room. All it would take is switching the box around inside the wall and moving the faceplate. Maybe not as easy a punching a hole in the wall, but if you're going to bust stuff up anyway at least this would be to code.
Posts: 6,572
Threads: 575
Joined: Jun 2024
Until recently, I was running 4 dual CPU Macs, 4 22" CRT's, 24 external hard drives, lights, network switches and a small fridge all from one 15A line.
We just added a new 20A line to the room
Posts: 21,885
Threads: 1,109
Joined: Mar 2024
Reputation:
0
And nothing blew up right? See, so you're probably fine MAVIC. Just make sure your power cords are not covered up or feel hot.
Posts: 21,860
Threads: 1,734
Joined: May 2025
Reputation:
0
Thanks guys. The one main rule I'm breaking is daisy chaining. I've got plug strips plugged into the two pass through plugs on one UPS, and one plug strip plugged into a pass through port on the other UPS. This all comes off one outlet since the others are difficult to get to. Most stuff is very low wattage, and nothing too power hungry runs off a plug strip or extension cord.
I think I will just put in outlet in from the other room.